Skip to content
Queensferry

Module 20 · Lesson 20.2

Checking a dynamic result

Six checks in order, what each one catches, and how to write them down so someone else can repeat them.

Why this matters

Analysis software does not report uncertainty. It reports a period to four decimal places whether the model is right or not, and it plots a mode shape just as neatly for a mechanism as for a building.

Every fault in this lesson has occurred on real projects, and every one of them produces output that looks entirely normal. What catches them is not experience or intuition — it is a short sequence of checks, run in a fixed order, every time.

This is the last lesson of the course, and it is the one that decides whether everything before it was useful.

By the end of this lesson you should be able to

  • Run six checks in order on any dynamic analysis output
  • Identify the specific fault each check catches
  • Recognise the signature of a missing constraint or an accidental mechanism
  • Record checks so that another engineer can repeat them

What you should already know

  • Modelling decisions (Lesson 20.1)
  • Effective modal mass (Module 11)
  • Time step and convergence (Module 8)
  • Base shear coefficient (Module 15)

Check 1: the first period against a hand estimate

Always first, because everything else depends on it.

For a moment frame, T ≈ 0.1N seconds, N being the number of storeys. For any building, T ≈ 0.075H^0.75 with H in metres. For a stiff shear-wall building, expect something rather shorter.

What a mismatch means:

Reported period much SHORTER than expected — the model is too stiff. Gross concrete properties, an accidental restraint, missing releases, or a rigid diaphragm applied where it does not belong.

Reported period much LONGER than expected — the model is too soft, or too heavy. Missing members, an unintended mechanism, missing connectivity, or a mass error.

If check 1 fails, stop. There is nothing to be learned from the rest of the output until the model is right.

Check 2: the seismic mass

Take the software's total seismic weight, divide by the plan area and the number of floors. For an ordinary building expect 8 to 15 kN/m².

Much lower — mass is missing. Superimposed dead not applied, cladding forgotten, or the mass source set to self weight alone.

Much higher — factored loads have been used as the mass, or the full imposed load rather than the quasi-permanent fraction.

This check is independent of everything else in the model, which is what makes it valuable.

Check 3: the first-mode effective mass

For a regular building, the first mode should carry 60% to 85% of the total mass. For a base-isolated building it should carry nearly 100%.

Very low, under about 20% — the reported first mode is almost certainly a local mechanism, not a global mode. An unrestrained member vibrating on its own, a node connected to nothing, a slab element with no in-plane stiffness. Plot the mode shape: a local mechanism moves one small part of the structure and leaves the rest still.

Above about 90% for a multi-storey building — suspiciously high. Usually means the model has been over-constrained into behaving like a single mass.

Check 4: the base shear coefficient

V/W, the base shear divided by the seismic weight. For an ordinary building under a design earthquake, expect roughly 0.02 to 0.5.

Outside that range, assume a unit error until proved otherwise. The classic is a spectrum entered in g when the software expects m/s², or the reverse — a factor of 9.81, which turns a plausible 0.15 into either 1.5 or 0.015. Both are immediately visible in this check and almost invisible everywhere else.

This is the single most effective check in the list, because it tests the whole chain — mass, spectrum, units, combination — with one number.

Check 5: cumulative effective mass

Sum the effective masses of the modes retained. Codes require at least 90% in each direction, and that is a MINIMUM for base shear.

If floor accelerations are wanted, 90% is not enough. Acceleration is dominated by higher modes that carry almost no effective mass, so the criterion that establishes the base shear says nothing about whether the accelerations have converged. Add modes until the acceleration stops changing, and report by how much it changed.

Check 6: the time step, and convergence

For a time-history analysis: Δt ≤ T/20 for the highest mode retained, not the first. Then halve the step, rerun, and report the change in the quantity that governs.

A statement that the analysis converged is not a check. A statement that halving the time step changed the peak drift by 0.3% and the peak floor acceleration by 1.1% is a check, and it is one a reviewer can weigh.

Faults with distinctive signatures

Missing diaphragm constraint. First frequency far too low; the mode shape shows a floor distorting in plane rather than translating; wildly uneven distribution of shear between the vertical elements.

Accidental mechanism. A cluster of near-zero-frequency modes with negligible effective mass, all localised to one place.

Unit error in the spectrum. Base shear coefficient out by a factor near 9.81, or near 1 000, or near 1 000 000.

Mass error. Period out by roughly the square root of the mass ratio; base shear out by roughly the mass ratio.

Over-constraint. Period too short, first-mode effective mass too high, drifts too small.

Too few modes. Base shear plausible, floor accelerations far too low, and the cumulative mass table shows why.

Writing it down

A check that is not recorded did not happen, as far as anyone reviewing the work is concerned. For each one, record: what was checked, what value the model gave, what was expected and on what basis, and whether it passed.

The expectation and its basis are the parts that get left out, and they are the parts that make the record useful. 'First period 0.87 s; expected 0.8 to 0.9 s from 0.1N and 0.075H^0.75; pass' can be repeated by anyone. 'Period checked, OK' cannot be repeated by anybody, including its author six months later.

Worked example

Auditing an analysis output, in order

Given

  • A ten-storey concrete frame, 34 m tall, plan 30 m × 20 m
  • Software reports: T₁ = 0.42 s; total seismic weight 41 000 kN; first-mode effective mass 78%
  • Base shear 21 500 kN; cumulative effective mass over 12 modes: 96%
  • The analysis is a response-spectrum analysis for a design earthquake

Find

Whether the output can be accepted, and if not, what is wrong.

Assumptions

  • Ordinary regular concrete frame on firm ground

    Predict first

    A modal analysis reports a first mode with a period of 4.8 s and an effective mass of 3%. The building is a six-storey steel frame. What is the most likely explanation?

    Practice

    A ten-storey building 34 m tall reports a first period of 0.42 s. What does the rule T ≈ 0.075H^0.75 predict, in seconds?

    Practice

    An analysis reports a base shear of 21 500 kN on a building of seismic weight 41 000 kN. What is the base shear coefficient?

    Practice

    A reported period is 0.42 s where 1.0 s was expected. By what factor is the model's stiffness in error?

    Practice

    A building of plan area 600 m² and ten floors has a reported total seismic weight of 41 000 kN. What is the seismic weight per unit floor area, in kN/m²?

    Check yourself

    A response-spectrum analysis gives a base shear coefficient of 1.6. What is the most likely cause?

    Check yourself

    Cumulative effective mass reaches 92% at mode 8. The analysis must produce floor accelerations for equipment qualification. What should be done?

    Check yourself

    Which of these checks is independent of the stiffness model, and therefore useful when the period check has already failed?

    Worked example

    Three checks on a reported frequency

    Given

    • A model reports a fundamental frequency of 4.8 Hz for a 12 m span composite floor

    Find

    Whether to believe it

      Worked example

      A frequency that came out too high

      Given

      • A concrete floor model reports 9.5 Hz
      • The 18/√δ estimate gives 6.0 Hz
      • The two disagree by 58 %

      Find

      Where to look

        Summary

        • Check the period against a hand estimate first; if it fails, stop
        • Check the seismic mass independently — 8 to 15 kN/m² for an ordinary building
        • First-mode effective mass under 20% means a local mechanism, not a global mode
        • Base shear coefficient outside 0.02–0.5 is a unit error until proved otherwise
        • 90% cumulative mass is a base-shear criterion and says nothing about accelerations
        • Convergence is demonstrated by rerunning and reporting the change, not asserted
        • Record what was checked, what was found, what was expected and on what basis
        Progress is kept in this browser only.

        This is educational material. It uses simplified examples to teach principles, and must not be relied on for real design or safety-critical decisions. Module overview and checkpoint