Module 1 · Lesson 1.2
Where dynamics actually matters in practice
The loadings that cause real problems, what each one does, and why most of them threaten usability rather than collapse.
Why this matters
It is easy to leave a first dynamics lesson thinking the subject is about earthquakes. Earthquakes are the most demanding application and they are not the most common. Most engineers who need dynamics need it for a floor that bounces, a bridge that people can feel, a chimney that hums in the wind, or a machine whose foundation is transmitting vibration into the building next door.
Almost none of those are strength problems. They are problems of usability, of comfort, of the equipment that has to work in the building, and — over years — of fatigue. Recognising which kind of problem you have decides which analysis you need, and the two are often confused.
By the end of this lesson you should be able to
- Name the common sources of structural dynamic loading and their frequency ranges
- Distinguish periodic, transient and random loading
- Explain why most dynamic problems in buildings are serviceability problems
- Recognise fatigue as a consequence of vibration rather than a separate subject
- Say what structural monitoring can and cannot tell you
Three kinds of loading
Periodic loading repeats. Rotating machinery, a reciprocating pump, a person walking at a steady pace. It is the dangerous class, because if its frequency happens to coincide with a natural frequency the response builds up cycle after cycle. Resonance is only possible with loading that repeats.
Transient loading happens once. A dropped load, a vehicle impact, a blast, a sudden change of support. The structure responds and then rings down. The peak response is what matters, and it usually occurs within the first cycle.
Random loading has no repeating pattern. Wind turbulence, earthquake ground motion, a crowd. It contains energy over a broad band of frequencies, so it will excite whatever natural frequencies lie in that band — but it does so intermittently rather than building up steadily.
The sources, and what they do
Pedestrian loading. People walk at 1.6 to 2.4 Hz, and run at 2 to 3.5 Hz. A footbridge or a long-span floor with a vertical natural frequency in that range will be excited directly. Worse, the second harmonic of walking lands around 4 Hz, which catches many composite floors. Lateral excitation is a separate problem at about half the pacing rate — around 0.9 Hz — and it is the mechanism behind the well-known lateral instability of some slender footbridges under crowds.
Machinery. A machine running at 1 500 rpm forces at 25 Hz. Rotating unbalance is the usual mechanism, and its force amplitude grows with the square of the speed, so a machine that is quiet at half speed can be violent at full speed. The critical period is start-up and shut-down, when the machine sweeps through every frequency below its running speed — including, possibly, the structure's.
Traffic and rail. Vehicles excite bridges both by their own weight moving across (which is a moving-load problem, not necessarily a vibration one) and by bouncing on their suspensions at 1 to 4 Hz. Rail is more demanding: sleeper passing frequencies and wheel flats produce narrow-band excitation at frequencies that can be predicted and must be checked.
Wind. Two distinct mechanisms, often confused. Buffeting by turbulence is broad-band random loading, and it excites whatever is there. Vortex shedding is periodic: a bluff body sheds vortices at a frequency proportional to wind speed, and at one particular speed that frequency coincides with a natural frequency and the response locks in. Chimneys, masts and circular sections are the classic sufferers.
Construction vibration. Piling, compaction, demolition and blasting produce ground-borne vibration that is transmitted into neighbouring structures. The concern is rarely the structure itself; it is the occupants, the sensitive equipment and — increasingly — the legal threshold agreed before work started.
Impact and blast. Short-duration, high-magnitude transient loading. Blast is included in this course as context only: it needs nonlinear analysis at strain rates where material properties themselves change, and it is a specialist subject.
Earthquake. Ground acceleration applied at the base, broad-band, lasting tens of seconds. The demanding case, and the reason for Stage C of this course.
Fatigue: the long-term consequence
A vibrating structure is a structure being cycled. At 3 Hz, a footbridge experiences about 10 million cycles a year of whatever stress range the vibration produces. Steel details have finite fatigue lives at stress ranges far below yield, and a detail that is perfectly adequate for a static check can accumulate damage indefinitely under a stress range of a few tens of newtons per square millimetre.
Fatigue is not a separate subject that happens to involve vibration. It is what vibration does over time, and the link between them is the stress RANGE and the number of cycles — both of which come out of a dynamic analysis and neither of which appears in a static one.
Monitoring: what it can and cannot tell you
Accelerometers on a structure will give you, reliably: natural frequencies, mode shapes if enough sensors are used, and damping ratios at the amplitude of the measurement.
They will not give you, without a great deal more work: the stress in any member, the loading that caused the response, or the damping at any other amplitude. Damping in particular is amplitude-dependent — a small-amplitude ambient test on a building typically reports 1 to 2%, and the same building in a storm may show 3 to 5%, because friction in cladding, partitions and joints only engages once things move enough.
That gap between measured and design damping is a recurring theme in this course, and it is the reason damping is the least reliable number in any dynamic model.
Predict first
A long-span office floor is found to bounce noticeably when people walk across it. Its natural frequency is 4.6 Hz. Which change is most likely to fix it?
Worked example
Is this floor going to be a problem?
Given
- An open-plan office floor, 12 m span composite beams at 3 m centres
- Calculated fundamental vertical frequency: 4.3 Hz
- Damping estimated at 3% (bare floor with light partitions)
- Occupancy: normal office use, some walking traffic across the bay
Find
Whether a vibration problem is likely, and what would change the answer.
Assumptions
- The calculated frequency is for the bare structure plus a realistic allowance for permanent fit-out mass
- Human comfort thresholds are taken as design guidance, not as absolute limits
Practice
A machine runs at 1 200 rpm. What is its forcing frequency in Hz?
Practice
A floor has a natural frequency of 5.0 Hz and 2% damping. If a harmonic force is applied at exactly that frequency, by what factor is the response amplified compared with the same force applied slowly?
Check yourself
Which of these loadings can produce true resonance?
Summary
- Loading is periodic, transient or random, and only periodic loading can truly resonate
- Pedestrians excite at 1.6–2.4 Hz and their second harmonic catches many floors near 4 Hz
- Most dynamic problems in buildings are comfort problems, at stresses far below any limit
- Depth raises frequency; strength does not; mass lowers it
- Fatigue is what vibration does over time, through stress range and cycle count
- Measured damping depends on amplitude, which is why design damping is uncertain