Module 18 · Lesson 18.2
Sizing and placing dampers
Where a damper earns its keep, how much damping it actually adds, and what analysis a damped structure needs.
Why this matters
A damper only works if the two ends of it move relative to one another. That obvious statement decides almost everything about where dampers go, and it is the single point most often got wrong in a retrofit.
Dampers are frequently placed where there is room for them — a plant floor, a stair core, a storey with a convenient bay. If that storey happens to have little inter-storey drift, the damper is an expensive ornament.
This lesson is about placing them where the structure is actually moving, quantifying what they add, and knowing what analysis is then required.
By the end of this lesson you should be able to
- Compute the damping ratio a linear damper adds to a mode
- Use modal drift to decide where dampers go
- Explain why added damping is mode-specific
- State the analysis a damped structure needs and why
What you should already know
- Damper force and energy per cycle (Lesson 18.1)
- Mode shapes and modal mass (Module 11)
- Classical and non-classical damping (Module 12)
The added damping ratio
For linear dampers, the damping ratio added to mode n is
ζadded = Σj Cj cos²θj φ²_rel,j / (2 ωn Mn)
where φrel,j is the relative modal displacement ACROSS damper j — the difference in the mode shape between its two ends — and Mn is the modal mass.
Every term in it is worth reading as a design instruction.
Cj, linear. Doubling the damper doubles its contribution. Predictable and unexciting.
cos²θj. Brace geometry, from the previous lesson. A damper at 60° retains 25% of the effectiveness of a horizontal one — and 60° is not an unusual angle in a tall narrow bay.
φ²_rel,j, SQUARED. This is the dominant term and the one that decides placement. A damper in a storey with twice the modal drift contributes four times as much.
1/ωn. Higher modes receive less added damping from the same damper — the opposite of what many people expect, and it follows directly from the modal mass and frequency in the denominator.
Mode-specific. There is no single 'added damping' for the structure. Each mode gets its own, and a damper layout tuned to the first mode may do very little for the second.
The squared modal-drift term is why damper placement is a modal question, not an architectural one. Plot the mode shape, look at the drift in each storey, and put the dampers where the drift is largest.
Placement in practice
Compute the modal drift in every storey for the modes that matter, and rank them. A first-mode-dominated shear building has its largest drift in the lower storeys, so that is usually where the dampers go. A building with a soft storey has almost all of its drift there, and a damper in that storey does an enormous amount.
Two qualifications that stop this being purely mechanical:
Do not tune only to the first mode. If the second mode matters — for floor accelerations, for a tall building, for torsion — check the added damping in that mode too. A layout that is excellent for mode 1 can be nearly useless for mode 2 if the dampers sit near mode 2's node.
Damper force has to go somewhere. A damper delivers a large force into the beam and column it connects to. Those members and their connections need checking for it, and a retrofit that concentrates all the dampers in one storey concentrates all that force there too.
Dampers add damping without adding stiffness
This is the property that distinguishes damping from bracing as a retrofit strategy.
Add a brace, and the storey stiffens. The period shortens, the structure moves UP the acceleration branch of the spectrum, and it attracts more force. It also attracts more force to the foundation, which on an existing building is frequently the binding constraint.
Add a viscous damper, and the period is essentially unchanged. The structure attracts the same spectral acceleration and responds less because it is dissipating energy. Nothing new is demanded of the foundation.
For a retrofit where the foundations cannot be strengthened economically, that difference decides the strategy.
What analysis is required
Linear dampers, and classical damping. If the damper layout happens to produce a damping matrix that the modes diagonalise, modal superposition survives and a spectrum analysis with modified modal damping is defensible. This is rare, and it must be TESTED rather than assumed — the orthogonality check from Module 12 answers it directly.
Linear dampers, non-classical damping. The usual case with concentrated dampers. The modes no longer decouple. Either use complex modal analysis, or run a direct integration.
Nonlinear dampers. No modal damping ratio exists at all. A nonlinear time-history analysis is required, and it is not optional.
The commonest error in damped-structure analysis is to compute an added damping ratio, put it into a response-spectrum analysis, and report the result. For concentrated dampers the damping is non-classical, the spectrum method's central assumption is violated, and the answer is not conservative in a knowable direction.
How much damping is worth adding
Response falls roughly as 1/ζ at resonance, so the returns diminish sharply.
Going from 2% to 10% cuts the resonant response by a factor of five. Going from 10% to 20% cuts it by a further two. Going from 20% to 30% gains a third. Beyond about 30% the dampers are large, the forces they impose on the frame are large, and the additional benefit is small.
Most supplemental damping schemes target 15% to 25% total, and that is a considered engineering target rather than a limit of the technology.
Worked example
Placing dampers by modal drift
Given
- A five-storey shear building, first mode ω₁ = 4.19 rad/s, modal mass M₁ = 900 tonnes
- First-mode shape, normalised to unity at roof: 0.20, 0.44, 0.66, 0.85, 1.00
- Linear dampers available with C = 2.0 MN·s/m, braced at 30°
- Target: at least 5% added damping in the first mode
Find
Which storeys to damp, and the damping added.
Assumptions
- Linear dampers; added damping evaluated for the first mode only at this stage
Predict first
A damper is moved from a storey with 0.24 modal drift to one with 0.12. What happens to its contribution to added damping?
Practice
A linear damper with C = 2.0 MN·s/m braced at 30° spans a storey with first-mode relative displacement 0.35. The first mode has ω₁ = 4.19 rad/s and modal mass 900 tonnes. What damping ratio does it add?
Practice
What fraction of a horizontal damper's effectiveness is retained by one braced at 60°?
Practice
A structure has 2% inherent damping. Six dampers add 5.81%. By what factor does the resonant response fall, taking response at resonance as proportional to 1/ζ?
Check yourself
Why might viscous dampers be preferred to added bracing in the seismic retrofit of an existing building?
Check yourself
Two dampers are quoted with the same coefficient C but different velocity exponents. What can be concluded?
Worked example
Where to put a damper in a three-storey frame
Given
- A three-storey frame, first mode shape roughly 0.33, 0.67, 1.00 from bottom to top
- One damper is available, and it acts on the drift of the storey it is in
Find
Which storey it should go in
Summary
- ζadded = Σ C cos²θ φ²_rel / (2ωM), and the squared drift term dominates
- Place dampers by modal drift, not by mode-shape ordinate or by available space
- Added damping is mode-specific; check the modes that matter, not just the first
- Dampers add damping without stiffness, so the foundations see no new demand
- Concentrated dampers give non-classical damping — test it, do not assume it
- Nonlinear dampers require nonlinear time-history analysis
- Returns diminish as 1/ζ; most schemes target 15–25% total
This is educational material. It uses simplified examples to teach principles, and must not be relied on for real design or safety-critical decisions. Module overview and checkpoint