Skip to content
Queensferry

Module 11

Steel–concrete composite beams

Make the slab work with the beam instead of sitting on it and the moment resistance nearly doubles for the price of some studs. The catches are all in the sequence: what carries what, and when.

What this module covers

  • Explain composite action physically, in terms of where the neutral axis moves
  • Calculate the plastic moment of a composite section and say which case is efficient
  • Say what a shear stud has to do and the two ways it can fail
  • Explain why partial shear connection is legitimate and often economic
  • Separate the construction stage from the composite stage, and say which governs
  • Explain why an unpropped beam's deflection cannot be calculated in one go

Lessons

  1. The slab is already there. Connect it to the beam and the two act as one section — with the concrete doing what it is good at and the steel doing what it is good at.

    Start lesson →
  2. Before the concrete sets, the beam is bare steel carrying wet concrete with nothing holding it sideways. That stage frequently governs — and it leaves a deflection behind that never goes away.

    Start lesson →

Module checkpoint

Check what you have taken in

8 questions

  1. Question 1

    A composite beam has Ma = 500 kNm bare steel and MRd = 900 kNm with full connection. With η = 0.5, what is MRd in kNm?

  2. Question 2

    Beams are at 4.0 m centres on a 10.0 m span. What is beff, in mm?

  3. Question 3

    A steel section of 12 000 mm² in S355 develops Na in tension. How many 80 kN studs are needed over the half span for full connection?

  4. Question 4

    A composite section is 3.26 times stiffer than the bare steel beam. If the same load acted on each, by what factor would the deflection fall?

  5. Question 5

    The short-term modular ratio is 6.4 and creep triples it. What is the long-term modular ratio?

  6. Question 6

    A beam deflects 20 mm in total over a 9.0 m span. What is its span-to-deflection ratio?

  7. Question 7

    Which check most often governs the construction stage of an unpropped composite beam?

  8. Question 8

    Why must transverse reinforcement cross the plane beside the studs?