Bolts, pins and welds

A fastener does not have a resistance. It has several, belonging to different failure modes in different materials — and which one governs decides what would actually help.

What this module covers

  • Say what happens at a bolt in shear, and why bearing is a separate check
  • Explain why a higher bolt grade often buys almost nothing
  • Recognise punching shear and prying, the two modes people forget
  • Explain what a preloaded bolt does differently, and why it is not chosen for strength
  • Size a fillet weld on its throat, and say what the directional method adds
  • Say what each detailing rule protects, rather than memorising the number

Lessons

  1. The bolt can shear, the plate can tear, the head can punch through, and a flexible plate can pry. Each is a different calculation with a different remedy.

    Start lesson →
  2. A preloaded bolt does not carry shear at all. A fillet weld is smaller than it looks. And every spacing rule is protecting a number in a calculation you have already done.

    Start lesson →

Module checkpoint

Check what you have taken in

8 questions

  1. Question 1

    An M24 grade 8.8 bolt has As = 353 mm², threads in the shear plane. What is Fv,Rd in kN? Take αv = 0.6, γM2 = 1.25.

  2. Question 2

    A bolt group has bolt shear 94 kN and ply bearing 60 kN per bolt. Six bolts carry the load. What is the group's resistance, in kN?

  3. Question 3

    What is the throat of a 10 mm equal-leg fillet weld, in mm?

  4. Question 4

    A 6 mm fillet gives 1067 N/mm longitudinally. What does a 200 mm run on each side of a plate give in total, in kN?

  5. Question 5

    A weld leg is doubled from 6 mm to 12 mm. By what factor does the deposited weld metal increase?

  6. Question 6

    An M20 bolt takes a 22 mm hole. What is the minimum end distance at 1.2 d₀, in mm?

  7. Question 7

    A bolted connection is governed by ply bearing. Which change would help most?

  8. Question 8

    Why is a fillet weld's strength taken on its throat rather than its leg?