Module 17 · Lesson 17.1
Moving loads: a member with no critical section
Everything so far has had a worst point you could find and check. A crane girder does not — the worst point depends on where the crane is standing.
Why this matters
Every member in this course so far has had a critical section: a point where the moment is largest, which you find once and then check. A crane girder does not. The load walks along it, and the maximum moment occurs at a position that depends on where the wheels happen to be — a position that is neither mid-span nor obvious. Finding it is a short and rather satisfying piece of mechanics, and getting it wrong by assuming mid-span is not conservative in the way people expect.
By the end of this lesson you should be able to
- Say why a moving load has no fixed critical section
- Find the absolute maximum moment from a wheel group
- State the classical equidistant condition
- Say what the dynamic factors represent
What you should already know
- Influence lines and moving loads — the Structural Analysis Fundamentals course covers these
- Crane actions, vertical and horizontal (Module 2)
- Bending resistance and the class-appropriate modulus (Module 6)
The load walks
A gantry crane runs on rails carried by girders. The crane has wheels — typically two per rail, at a fixed spacing — and it can stand anywhere along the span.
So the question "what is the maximum moment?" has two unknowns rather than one: where along the beam, and where is the crane. Both have to be searched.
Two things about the answer surprise people.
It is not at mid-span. For a two-wheel group at 3.5 m spacing on a 12 m span, the maximum occurs 5.125 m from the support — 875 mm off centre. The offset depends on the wheel spacing, and for a three-wheel group it can be somewhere else again.
It is not what a single equivalent load would give. Putting the whole group at mid-span as one load gives 955 kNm; the real answer is 697 kNm. The guess is 37% high — conservative here, but it is conservative by accident rather than by design, and for other configurations the relationship goes the other way.
A moving load has to be searched. Neither the position nor the magnitude can be reasoned to.
Try it
Where the maximum actually is
The curve is the largest moment anywhere on the beam as the wheel group walks across it. The peak is what the girder must be designed for — and where it occurs is not mid-span.
- Resultant of the group
- 318 kN
- Maximum moment
- 696.0 kNm
- Occurs at
- 5.125 m
- Mid-span is at
- 6.000 m
- Offset from mid-span
- 875 mm
- Under which wheel
- wheel 1
- Wheel to resultant
- 1750 mm
- Classical condition predicts
- 875 mm
- Whole group on the span
- yes
- Discrepancy
- 0 mm
- Same total at mid-span
- 954.0 kNm
- That guess is high by
- 37 %
The absolute maximum moment is 696 kNm, occurring 5.13 m from the left support under wheel 1 — NOT at mid-span. Putting the whole group at mid-span as a single load would have given 954 kNm, which is 37% higher — a moving load has no fixed critical section, and neither the position nor the magnitude can be guessed.
Things worth trying
- Start at the defaults — 12 m span, 3.5 m spacing, equal 159 kN wheels. The peak is 697 kNm at 5.125 m: 875 mm off mid-span.
- Check the discrepancy row. The numerical search and the classical closed form agree to a millimetre, and they are entirely different calculations.
- Compare with the last row: putting the same total at mid-span gives 955 kNm, 37% high. Conservative here — and by accident, not design.
- Now bring the wheel spacing down to 0.5 m. The group becomes a single load, the peak moves to mid-span, and the 'guess is high by' figure falls to nearly zero.
- Take the spacing out to 8 m on a 12 m span. Only one wheel is now on the span at the critical position, and the readout says the classical condition no longer applies — it assumes the whole group is on. The search is still right; there is just nothing to check it against.
- Make the trailing wheel much heavier than the leading one. The critical position moves to the heavy wheel — the group's resultant has shifted and the condition follows it.
- Shorten the span to 6 m with 3.5 m spacing. The two wheels barely fit, and the whole character of the answer changes.
- Watch the discrepancy stay near zero throughout. That is a check on the search running continuously, which is what makes the numerical answer trustworthy.
Worked example
A 12 m crane gantry girder
Given
- 12.0 m simply supported gantry girder
- Overhead crane: 200 kN self-weight, 300 kN hoist load, hoisting class HC2
- Two wheels per rail at 3.5 m spacing
- Girder trial section 610 × 229 × 113 UB in S355
Find
The maximum moment, where it occurs, and whether the trial section works.
Assumptions
- Dynamic factors are calibrated and unverified here, so the calculation is teachable rather than usable
- The crane is assumed central on its rails, so each rail takes half the load
- Horizontal surge and the rail's own effects are separate checks not covered here
Practice
A crane has 200 kN self-weight and 300 kN hoist load, with φ₁ = 1.10 and φ₂ = 1.39. What is the dynamic vertical action, in kN?
Practice
That action is shared over two rails with two wheels on each. What is the wheel load, in kN?
Practice
A single 637 kN load at mid-span of a 12 m beam, shared over two rails, gives what moment per rail, in kNm?
Practice
The critical wheel sits 875 mm from mid-span on a 12 m span. Where is it, measured from the left support, in m?
Check yourself
Why is the maximum moment from a moving wheel group not at mid-span?
Summary
- A moving load has no fixed critical section — both position and load position must be searched
- The maximum occurs UNDER a wheel, never between wheels
- Classical condition: that wheel and the resultant equidistant about mid-span
- For the worked girder: 697 kNm at 5.125 m, 875 mm off centre
- The search and the closed form agreed to the millimetre
- The single-load-at-mid-span guess gave 955 kNm — 37% high, and conservative by accident
- Dynamic factors are inertial effects, not margins: 637 kN against a static 500
- The trial girder passed bending at 0.54, and is not adequate
This is educational material. It uses simplified examples to teach principles, and must not be relied on for real design or safety-critical decisions. Module overview and checkpoint