Module 12 · Lesson 12.1
Earth pressure
Why the load on a retaining wall depends on the wall, and why water is the thing that actually breaks them.
Why this matters
Every other structure in this course has a load that exists independently of the structure. A retaining wall does not: the pressure it attracts depends on how far it moves, and a wall that cannot move attracts half as much again. Get that wrong and the wall is under-designed by 50% before any calculation begins — and no check anywhere will reveal it, because the calculation will be perfectly consistent with the wrong assumption.
By the end of this lesson you should be able to
- State the three pressure states and the movement each requires
- Compute the active, at-rest and passive coefficients
- Explain why water is more severe than soil
- Identify which quantities come from the ground investigation
What you should already know
- Mohr's circle and principal stresses (Structural Analysis Fundamentals, Module 13)
- Bearing pressure and the middle third (Module 11)
Three states, decided by movement
Soil behind a wall is not in one fixed state. What it does depends on what the wall does.
At rest. The wall has not moved. The soil is in the state it was left in by deposition and compaction, with horizontal stress a fixed fraction of vertical stress. K₀ ≈ 1 − sin φ.
Active. The wall yields away from the soil. The soil expands laterally, mobilises its shear strength, and the horizontal stress falls to a minimum. Ka = (1 − sin φ)/(1 + sin φ).
Passive. The wall pushes into the soil. The soil is compressed laterally, its shear strength again resists, and the horizontal stress rises to a maximum. Kp = 1/Ka.
For a 30° soil these are 0.50, 0.33 and 3.00. The spread is enormous — a factor of nine between active and passive — and which one applies is decided entirely by movement.
What it calculates: The ratio of horizontal to vertical effective stress in the active state.
- Angle of shearing resistance of the soil (degrees)
- Ka
- Active earth pressure coefficient (—)
This assumes
- Cohesionless soil, or cohesion conservatively ignored
- Smooth vertical wall back and horizontal ground surface
- The wall has moved enough to mobilise the active state
- DERIVED from the Mohr circle at failure — not empirical
In plain terms: The two forms are identical, and the second is worth knowing because the 45° − φ/2 is the angle of the failure plane in the soil. The coefficient is not a fudge factor: it is the ratio of the two principal stresses when a soil element is on the point of failing.
Try it
Check a retaining wall
Three stability checks at once. Move one slider and watch them trade against each other — then raise the water table, which is what most retaining walls actually fail on.
Wall movement
- Coefficient (active)
- 0.333
- Horizontal force
- 91.7 kN/m
- Vertical load
- 253.2 kN/m
- Overturning moment
- 167 kNm/m
- Restoring moment
- 497 kNm/m
- Overturning factor, need 2.0
- 2.98
- Sliding factor, need 1.5
- 1.38
- Resultant in middle third?
- yes
- Peak bearing pressure
- 123 kPa
Inadequate, governed by sliding. Overturning 2.98 against 2.0; sliding 1.38 against 1.5.
Things worth trying
- Raise the water table to the top. The overturning moment nearly doubles and the wall fails outright — no amount of reinforcement would save it. Most retaining walls that fail, fail this way.
- Widen the base. Sliding and overturning both improve, because more soil sits on the heel to hold the wall down. Base width is the cheapest variable a retaining wall has.
- Switch to a propped wall. The at-rest coefficient is half as much again as the active one, so a basement wall designed for active pressure is under-designed by that margin.
- Raise H by one metre. The overturning moment goes with the CUBE of the height, so it is a far bigger change than it looks.
- Move the toe forward and back at fixed B. Sliding barely changes, but the resultant shifts and the bearing pressure redistributes — that is what the toe length is for.
Why water is the thing that breaks retaining walls
Soil pushes with K γ z. Water pushes with γw z — no coefficient at all.
That is not an oversight. A coefficient less than one exists because soil has shear strength: it can carry some of its own weight sideways through friction between grains. Water has no shear strength whatsoever, so it pushes with its full weight in every direction. K = 1, always.
Compare the two for a typical soil:
| Effective horizontal push per metre depth | |
|---|---|
| Drained soil, Ka γ | 0.33 × 18 = 6.0 kN/m³ |
| Water, γw | 9.81 kN/m³ |
Water pushes more than half again as hard as the soil it is sitting in. And when the water table rises, both act: the soil below it becomes buoyant, which relieves some of the earth pressure, but nowhere near enough to compensate.
A wall that is comfortable when drained can fail outright when the drainage blocks. Most retaining walls that fail, fail this way — not because the reinforcement was wrong, but because a filter drain silted up.
This is why the drainage behind a retaining wall is a structural detail, not a landscaping one.
Predict first
A drained 5 m wall has an overturning moment of 167 kNm/m. The drainage blocks and the water table rises to the top. Roughly what does the overturning moment become?
Practice
A soil has a friction angle of 35°. What is the active earth pressure coefficient Ka?
Practice
For that same 35° soil, what is the at-rest coefficient K₀?
Practice
A 5 m high wall retains soil with Ka = 1/3 and γ = 18 kN/m³. What is the horizontal force per metre run, in kN/m?
Check yourself
Why does water pressure use no earth-pressure coefficient?
Summary
- Three states — at rest, active, passive — decided by how far the wall moves
- For a 30° soil: K₀ = 0.50, Ka = 0.33, Kp = 3.00
- Active needs about 0.1% of the height in rotation; a propped wall cannot deliver it
- Ka is DERIVED from the Mohr circle, not fitted
- Water uses K = 1 because it has no shear strength
- Flooding roughly doubles the overturning moment, buoyancy notwithstanding
- φ, γ, base friction and bearing resistance are geotechnical inputs, not assumptions
This is educational material. It uses simplified examples to teach principles, and must not be relied on for real design or safety-critical decisions. Module overview and checkpoint