Skip to content
Queensferry

Module 11 · Lesson 11.2

Stiffness, and the piled raft

What a raft is actually good at.

Why this matters

If a raft increases total settlement, what is it for? The answer is in Module 10: buildings are damaged by differences in settlement, not by settlement. A raft is a device for converting a differential problem into a total one, and that trade is very often worth making.

Raft stiffness decides how much of that conversion actually happens.

A genuinely rigid raft settles as a plane. Wherever the ground is soft it sheds pressure to stiffer areas, and the differential settlement across the building approaches zero — at the cost of large bending moments in the raft itself, since it is now spanning between hard spots.

A flexible raft follows the ground. It attracts small moments and behaves as a collection of independent footings that happen to be joined, so it inherits the ground's variability more or less unchanged.

Real rafts sit between the two, and where they sit depends on the raft's thickness against the plan dimension and on the ground's stiffness. The important consequence is that raft moments and differential settlement trade against each other: you cannot reduce both at once by adjusting the raft alone.

The piled raft is the case where neither a raft nor a pile group is quite right.

The conventional approach is either/or: if the raft settles too much, replace it with piles designed to carry the whole load. A piled raft instead keeps the raft carrying most of the load and adds a smaller number of piles specifically as settlement reducers, placed where the settlement profile is worst — usually beneath the more heavily loaded central area.

The piles are deliberately loaded close to their capacity, which is unnerving the first time you meet it, but it is the point: a pile that is not fully mobilised is not doing the job it was added for. What the arrangement controls is the shape of the settlement, which is what the structure cares about.

Check yourself

A raft is made considerably thicker and stiffer. What happens to differential settlement and to the raft's bending moments?

Check yourself

In a piled raft, what are the piles for?

Try it

The compensated raft

Excavate to pay for the building — then see why the raft still settles more than a pad at higher pressure.

3.00 m
150 kPa
12.0 m

What is fixed

  • γ = 19 kN/m³, E = 25 MPa, ν = 0.3, rigid foundation.
  • The comparison pad is 2.5 m square at the full gross pressure.
Raft, gross 150 kPa68.2 mm
Raft, net 93 kPa42.3 mm
2.5 m pad at 150 kPa14.2 mm
Stress removed
57 kPa
Net pressure
93 kPa
Degree of compensation
38 %
Depth for full compensation
7.9 m
Raft settlement
42.3 mm
Pad settlement, for comparison
14.2 mm

The raft settles 42.3 mm at 93 kPa while the far smaller pad settles 14.2 mm at 150 kPa. Lower pressure, more settlement — because width, not pressure, sets the depth of ground that compresses.

Summary

  • Rafts are indicated when pads merge, when ground is variable, or when compensation is available
  • Compensation removes pre-existing stress: 3 m of excavation paid for 38% of the building
  • A raft settles more than a pad at lower pressure, because it stresses far deeper ground
  • Raft stiffness trades differential settlement against bending moment
  • A piled raft uses a few well-mobilised piles to reshape the settlement profile, not to carry the load
Progress is kept in this browser only.

This is educational material. It uses simplified examples to teach principles, and must not be relied on for real design or safety-critical decisions. Module overview and checkpoint